Floating ground ?

My wife and I just moved out of a crappy apartment and into a house(rental).
When talking with the landlord he told me that the house was built in 1925 and that currently the wiring while it has a circuit breaker installed it is only a two wire set-up.
One wire is hot and the other neutral, and does not have the third wire for ground.
Talking with a electronics tech. he said that my house could very well have a floating ground.
Well, how do I tell if it does have a floating ground and what would it affect?
Reply With Quote
  #2  
Old 06-15-2014, 09:40 PM
maxhifi's Avatar
maxhifi maxhifi is offline
VideoKarma Member
 
Join Date: Dec 2010
Posts: 1,869
I am not sure what he meant by that. The utility feed will certainly have the neutral and ground bonded together at both the transformer and the service entrance at
The house. Check voltage between hot and a water pipe or radiator pipe to check it, should be about 120 to ground. If you get any other value either the pipe
Isn't grounded or there's a problem with your electrical system.
Reply With Quote
  #3  
Old 06-16-2014, 07:23 PM
dieseljeep dieseljeep is offline
VideoKarma Member
 
Join Date: Jul 2010
Posts: 7,562
Quote:
Originally Posted by maxhifi View Post
I am not sure what he meant by that. The utility feed will certainly have the neutral and ground bonded together at both the transformer and the service entrance at
The house. Check voltage between hot and a water pipe or radiator pipe to check it, should be about 120 to ground. If you get any other value either the pipe
Isn't grounded or there's a problem with your electrical system.
Get the electric utility to come and check it out.
The owner might be mistaken about the service entrance. I don't know of any homes that still have a two wire 120 volt service. They only were good for 30 amps, max.
The 1959 code required a minimum 120/240 volt, 100 amp, three wire service, for residential applications. It didn't make any difference, how many circuits were used. I've seen 100 amp services, that only had, two 15 amp 120 volt branch circuits. They owner did it to satisfy the insurance company.
Reply With Quote
  #4  
Old 06-16-2014, 08:20 PM
earlyfilm's Avatar
earlyfilm earlyfilm is offline
Eternal Member
 
Join Date: Jun 2011
Location: Culpeper, VA
Posts: 527
Quote:
Originally Posted by radio nut View Post
Talking with a electronics tech. he said that my house could very well have a floating ground.
He means that some receptacles might be reversed.

With that said, unless you were talking about commercial use, there were no grounded receptacles back then, so any polarized receptacles in the house are modern, and they may be wired wrong.

Back in the day, most electricians did not bother to mark which wire was hot and which was ground, as you could put in the plug either way.

To the best of my knowledge, if the house was built to code, and no new outlets were needed, you could leave in place any wiring that met code when the house was built. The laws governing this vary from community-to-community.

(Floating ground can also refer to 120 taken off a three phase circuit, where neither side of the two wires is grounded. This happened in some early buildings, that had phase heavy motors and someone goofed while adding a circuit. I've only seen this in older commercial buildings, not in private homes.)

James

Last edited by earlyfilm; 06-17-2014 at 04:32 PM. Reason: Thought "phase" and wrote "wire"
Reply With Quote
  #5  
Old 06-17-2014, 09:53 AM
dieseljeep dieseljeep is offline
VideoKarma Member
 
Join Date: Jul 2010
Posts: 7,562
Quote:
Originally Posted by earlyfilm View Post
He means that some receptacles might be reversed.

With that said, unless you were talking about commercial use, there were no grounded receptacles back then, so any polarized receptacles in the house are modern, and they may be wired wrong.

Back in the day, most electricians did not bother to mark which wire was hot and which was ground, as you could put in the plug either way.

To the best of my knowledge, if the house was built to code, and no new outlets were needed, you could leave in place any wiring that met code when the house was built. The laws governing this vary from community-to-community.

(Floating ground can also refer to 120 taken off a three phase circuit, where neither side of the two wires is grounded. This happened in some early buildings, that had three wire heavy motors and someone goofed while adding a circuit. I've only seen this in older commercial buildings, not in private homes.)

James
Unless I've seen the wiring done in the home, it's hard to advise anyone.
I re-read the O/P and the owner was probably referring to the receptacles.
They were probably replaced with the newer grounding type. If the home was wired with the old style B/X cable, there might be, somewhat of a ground, but not a perfect one. If you meter the hot wire to the box, you'll get a reading.
If the home has knob and tube wiring or the old style romex without the ground wire and the receptacles, were replaced with grounding ones, it's a code violation.
Buy one of those simple, three light receptacle testers and it'll will indicate if the receptacle is wired properly.
Reply With Quote
Audiokarma
  #6  
Old 06-17-2014, 11:44 AM
radio nut's Avatar
radio nut radio nut is offline
Born in the wrong decade
 
Join Date: Dec 2007
Location: Lima, Ohio
Posts: 836
I will check the outlets with a tester this weekend. If not up to code...could the two wired outlets cause issues with my electronics?
Reply With Quote
  #7  
Old 06-17-2014, 12:54 PM
Username1's Avatar
Username1 Username1 is offline
Not sure how I got here.
 
Join Date: Dec 2009
Location: Orange County NY
Posts: 3,649
Quote:
If the home has knob and tube wiring .................
I would worry more about this little bit of funky wiring, and the possibility of
FIRE and less about your electronics.....

And looking at my own house, and some of the stories on VK about house wiring
It does not matter what the code is, what matters is WTF they actually did....
And if the stuff made back then has any surprises yet to show themselves
because you may put a greater demand on them than what previous owners
may have......

.
__________________
Yes you can call me "Squirrel boy"
Reply With Quote
  #8  
Old 06-17-2014, 01:25 PM
oldtvsandtoy oldtvsandtoy is offline
Banned
 
Join Date: Aug 2009
Location: Clinton Township , Michigan
Posts: 285
1st you can not have a floating ground, you have a floating neutral. In your panel a ground and neutral can be one of the same, in your house they can not. In the old days your chassis was use as a ground. So if you plug your cord in wrong your chassis would be hot, and you could get zapped. This has happen and people did get killed. That is why we use the 3 wire system today. Now with that said here in Michigan a house must be brought up to code to rent it out. 3 wire systems are code in a home. You need to call city hall to see what code in in Ohio. Most likely it's a 3 wire system, they will make the landlord bring the house up to code. Or he will not be able to rent it out. You should check it out.
Reply With Quote
  #9  
Old 06-17-2014, 01:37 PM
oldtvsandtoy oldtvsandtoy is offline
Banned
 
Join Date: Aug 2009
Location: Clinton Township , Michigan
Posts: 285
No you can have more then 30a on a two wire system. You just need to use bigger wire. A dryer can run on two wire 40a and a stove on two wire 60a
Quote:
Originally Posted by dieseljeep View Post
Get the electric utility to come and check it out.
The owner might be mistaken about the service entrance. I don't know of any homes that still have a two wire 120 volt service. They only were good for 30 amps, max.
The 1959 code required a minimum 120/240 volt, 100 amp, three wire service, for residential applications. It didn't make any difference, how many circuits were used. I've seen 100 amp services, that only had, two 15 amp 120 volt branch circuits. They owner did it to satisfy the insurance company.
Reply With Quote
  #10  
Old 06-17-2014, 02:03 PM
Kevin Kuehn's Avatar
Kevin Kuehn Kevin Kuehn is offline
Workin' Late Again
 
Join Date: Jan 2011
Location: WI
Posts: 3,976
What scares me more than the old two wire system's, is the modern code approved twisted(wire nut) connections, and those crazy push in terminals on the back of duplex receptacles.
Reply With Quote
Audiokarma
  #11  
Old 06-17-2014, 02:58 PM
maxhifi's Avatar
maxhifi maxhifi is offline
VideoKarma Member
 
Join Date: Dec 2010
Posts: 1,869
I think there is some confusion here. "two wire system" is being interpreted two ways, both of which are correct.

1. A "three wire service", is a 120/240V service. If you have a circuit breaker panel this is probably what you have. If you have an electric stove or dryer, this is definitely what you have. The "two wire service" which was 120V only, was a very simple service basically for lighting loads only, and it is very unlikely such a service would still be in existence. I haven't seen one since the 1980s and that was at a house which had been continuously occupied since the late 1930s... finding a two wire 120V service on a house these days is looking for a real antique.

2. "two wire receptacles" means receptacles without a third (grounding) prong. As previously mentioned, if someone at some time replaced the original two prong receptacles with three prong receptacles (as these are more commonly available), the third prong is connected to nothing and thus "floating".

I would imagine your friend is talking about scenario 2, so what to do about it?

1. With any "two prong" electronics this is an absolute non-issue

2. If you must, you can use a GFCI to connect three prong loads, it will detect any current to ground and perform the same job as a ground connection. The Canadian Electrical Code permits a GFCI to be used as a substitute for a ground connection in existing two wire installations - I am not sure if the NEC does or not, but it's a method to improve safety.

3. Add a ground connection to specific existing outlet. Get an appropriate length of #14 XLPE wire, and connect it from the third prong of the specific outlet being grounded back to a solid ground, such as the electrical panel enclosure, or a copper water pipe.

About wire nuts - my house was built in 1962 and all the "wire nuts" are just fine... wire nuts are fine anywhere except where there's vibration, if installed correctly. Push in terminals on receptacles though are just crap, I can't believe they ever got a UL/CSA approval

Last edited by maxhifi; 06-17-2014 at 03:16 PM.
Reply With Quote
  #12  
Old 06-17-2014, 04:31 PM
earlyfilm's Avatar
earlyfilm earlyfilm is offline
Eternal Member
 
Join Date: Jun 2011
Location: Culpeper, VA
Posts: 527
Quote:
Originally Posted by maxhifi View Post
3. Add a ground connection to specific existing outlet. Get an appropriate length of #14 XLPE wire, and connect it from the third prong of the specific outlet being grounded back to a solid ground, such as the electrical panel enclosure, or a copper water pipe.
Some locations require a grounding wire at the utility box and nowhere else. I got in a fight with the inspector in Memphis, because I grounded our washer and dryer to the copper cold water pipe instead of to the central ground. (Our washer and dryer were in an unheated, unfinished, concrete-floor utility room outside of the back of our house.) I did this because if something fails and the ground wire becomes hot and I wanted no possibility for a shock in this potentially wet area.

I then suggested to the inspector that I tie both together, and was told specifically that it was not permitted.

James
Reply With Quote
  #13  
Old 06-17-2014, 04:53 PM
wa2ise's Avatar
wa2ise wa2ise is offline
VideoKarma Member
 
Join Date: Dec 2002
Location: USA
Posts: 3,147
Quote:
Originally Posted by maxhifi View Post
...The "two wire service" which was 120V only, was a very simple service basically for lighting loads only, and it is very unlikely such a service would still be in existence. I haven't seen one since the 1980s and that was at a house which had been continuously occupied since the late 1930s... finding a two wire 120V service on a house these days is looking for a real antique. ...

Push in terminals on receptacles though are just crap, I can't believe they ever got a UL/CSA approval
My grandma's house, in 1984, had that 2 wire service. POCO cones into the basement, thru a 30A screw in fuse, then the meter, then to a pair of 15A fuses, and the neutral also had fuses, we used 30A fuses there, so the hot side 15A fuses would be the ones to blow. If we wanted to, we could have easily grabbed unmetered power at that first 30A fuse. But we didn't.

As for the push in terminals, I've heard electricians call them "Push and pray".
__________________
Reply With Quote
  #14  
Old 06-17-2014, 05:24 PM
maxhifi's Avatar
maxhifi maxhifi is offline
VideoKarma Member
 
Join Date: Dec 2010
Posts: 1,869
Quote:
Originally Posted by wa2ise View Post
My grandma's house, in 1984, had that 2 wire service. POCO cones into the basement, thru a 30A screw in fuse, then the meter, then to a pair of 15A fuses, and the neutral also had fuses, we used 30A fuses there, so the hot side 15A fuses would be the ones to blow. If we wanted to, we could have easily grabbed unmetered power at that first 30A fuse. But we didn't.

As for the push in terminals, I've heard electricians call them "Push and pray".
I am assuming 1894 - that's cool, my great grandparents house had that sort of a set up too, that's why they had a gas range and gas dryer.
Reply With Quote
  #15  
Old 06-17-2014, 05:30 PM
maxhifi's Avatar
maxhifi maxhifi is offline
VideoKarma Member
 
Join Date: Dec 2010
Posts: 1,869
Quote:
Originally Posted by earlyfilm View Post
Some locations require a grounding wire at the utility box and nowhere else. I got in a fight with the inspector in Memphis, because I grounded our washer and dryer to the copper cold water pipe instead of to the central ground. (Our washer and dryer were in an unheated, unfinished, concrete-floor utility room outside of the back of our house.) I did this because if something fails and the ground wire becomes hot and I wanted no possibility for a shock in this potentially wet area.

I then suggested to the inspector that I tie both together, and was told specifically that it was not permitted.

James
Yes, if you ground at more than one point you might create a ground loop, and get circulating currents. I said to ground to a pipe because realistically, it may be totally impractical to run a wire all the way back to the panel and there could be a water or radiator pipe staring you in the face. Of course I am assuming your water pipes are all metal and are grounded too, but given the age of the house it's probably a reasonable assumption.

Electrical code is designed in such a way as to be fool proof, but it is far from the only way to make something safe and reliable. Of course I am making the assumption that the pipe is a good ground, but it's not hard to verify if it is. Look at how wiring is done in Europe... much of it would NEVER pass inspection in north America but you don't hear scary statistics about electrical fires and electrocutions in Europe.
Reply With Quote
Audiokarma
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:03 AM.



Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2026, Jelsoft Enterprises Ltd.
©Copyright 2012 VideoKarma.org, All rights reserved.